Not 0 when mo power ! #37
-
Hi Just bought the complete kit and I'm quite impressed by quality of the board and design but I have an annoying issue. Even without CT connected or CT connected but laying on table, ESPHome reports some small consumptions on each input ! I have around 100W measured while it should be 0. Thanks Vincèn |
Beta Was this translation helpful? Give feedback.
Replies: 3 comments
-
Hi Vincèn, Thanks for supporting the project! It can be that you may need to play around the calibration coefficients associated to each CT clamp. @lucazeta1975 opened some days ago a nice discussion with some updated calibration factors, I'd recommend them to give them a try or check out the calibration procedure from the docs 😉😉. Let me know if this helps. PS: I'm converting this issue to a discussion as it fits better. |
Beta Was this translation helpful? Give feedback.
-
Hi @JGAguado Thanks a lot for your answer and for moving it as a discussion ;) For calibrations I have done it once installed in electrical panel and discussion of @lucazeta1975 confirms what I have done too. My only issue now is that once packed in electrical panel to be able to close it I have some small consmuptions measured that should not be there. Is it i a problem if CT are side by side or very near of each other ? Best Vincèn |
Beta Was this translation helpful? Give feedback.
-
I share my observations: |
Beta Was this translation helpful? Give feedback.
I share my observations:
#35 (comment)